Hi,

 

i was wondering could i have some of your thoughts on the following in relation to the analysis of a horizontal rigid floor diaphragm over a transfer structure or maybe someone has come across it before. If you have a shear wall layout at different floor levels on upper floors on a structure which the location of the bracing walls mirrors each floor level i.e. shear walls are in the same location the entire height of the building. However when you get to lower level the walls become blade column, thicker walls and some are located in different areas i.e. thus the horizontal load distribution on the lower floor level where the wall has change would be different to the walls above. For the lateral load distribution analysis of the lower wall level diaphragm, to find out how much load is allocated to each wall depending on its stiffness, would you apply the total horizontal load for the upper levels at the centre of rigidity of the upper walls, at the centre of rigidity location on the lower level diaphragm as one force in each direction, then just analyse the lateral loads at the lower level which are applied directly at that level separately.

 
I have previously always placed the total lateral load over transfer levels at the centre of rigidity of the upper wall layout., however now I am not too sure? Has anyone ever come across this in the past, analysing using hand calculations rather than software.  
 
As a really simplistic example basically if You had say a 30m x 30m square area on plan forming a floor diaphragm on upper levels of a building. At each one of this those levels You then have one bracing element only in the right hand corner of the 30m x 30m square. From this You apply say evenly distributed horizontal wind load across the face of the level applied at the centre of pressure I.e. Say 15m in from each side, the bracing member in the corner then takes all the loading based on its stiffness as per any general shear wall layout. The horizontal load acts at the bottom of this wall, and this diaphragm has a shear centre or centre of rigidity (say it works out at 3m in from right hand side as an example) at which the overall load acts away from the centre of pressure which is where eccentricity causes any torsion etc in the diaphragm.

So when you get to the bottom transfer level which is still a 30m x 30m square, however on this level you suddenly have 2 bracing elements one on the right hand side and one on the left hand side this time, thus the shear centre or centre of rigidity changes of the wall stiffness of the diaphragm changes, so my issue is that the loads applied directly at that level to the face of the transfer level are placed at the centre of pressure at that level say again 15m in from either side. However are the loads from the levels above which are also transferred through this level applied at shear centre of the above wall system (in this case say 3m in from right hand side as above) or at the centre of pressure on the wall system above which would be 15m in from either side? 

I would have thought that the total horizontal load above are applied at the shear centre of wall system above on the plan of the transfer level wall system below? And that's what I have assumed in the past when we construct buildings with transfer levels. Thanks in advance for any reolys on this one. 
 
S.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now
Sign in to follow this  
Followers 0

  • Recently Browsing   0 members

    No registered users viewing this page.

  • Similar Content

    • By Sidnum
      hi,
       
      I am designing a transfer beam 10m long with a permissible deflection of 5mm at 1/3 locations. the reason for such an onerous design requirement is to suit precast cladding that will be sitting on the beam.
      the beam is underneath an RC flat slab which picks up these load bearing precast panels.
       
      my question is what load combination can I use to check for deflection.
       
      If I were to design this as an RC element i could use the combination of 100% permanent and 30% variable for deflection as per Technical Report 58 from the concrete centre. seeing as the steel beam is picking up an RC flat slab which supports the precast elements I could see an argument for it!
       
      the eurocode isn't very clear on what combinations to use for steel for steel deflection check. 
      BS EN 1991-1-1:2002, equation 6.2, page 23 allows a reduction factor for variable load depending on the number of stories supported. in our case it would 70%-80%
       
      Looking forward to your assistance
       
       
       
    • By kalinnmg
      Hi there,
      I was trying to find information about how to calculate a plastic hinge between a bridge deck and its foundations. Is there anyone who has a methodology of how to perform these calculations? I'll be very glad to learn anything more about this type of connection detail.
    • By maths
      Hi all
      I have to design a reinforced concrete staircase which will be cast insitu. The client wants a cantilever staircase which means that it has to be transversely supported. The problem is that the wall is cavity 300mm brick and block. How is the steel reinforcement be fixed to the masonry wall to support the cantilever staircase ?
      Thanks
    • By orioltarros
      Hello, my name is Oriol Tarròs and I am a partner in a Barcelona based structural consultancy and specialized on prestressed concrete. I think this website is a great source of information and a very interesting place to share knowledge.
    • By RonnyRaygun
      I am struggling to find information on the structural class of a member.
      It seems that it is determined by exposure class and is used to define cover but can anyone give me information on how to make the classification?
      Thanks,